Different types of backflow prevention


A backflow prevention arrangement or device is in  effect a barrier intended to prevent contaminated fluid flowing backwards.

Backflow protection can be provided by an air or tap gap arrangement or a mechanical backflow prevention device approved be the Regulator (Regulators’ Specification), or alternatively authorised as a relaxation. (Relaxations allow a water undertaker the discretion to accept an arrangement as preventing backflow.)

The Regulators’ Specification not only provides definitions but also rates a backflow protection arrangement or device for suitability against contamination risk (fluid categories) and types of backflow risk - back siphonage or back pressure. They should always be accessible for inspection, maintenance and replacement.

Backflow prevention devices, are required to be corrosion resistant. For example, for metallic backflow prevention devices manufactured of gunmetal or other dezincification resistant materials. Dezincification water fittings are typically marked with a CR symbol.

As some backflow prevention arrangements and devices have operational limitations you should always check with the local water undertaker to make sure they are suitable for the intended application. Wherever practicable plumbing systems should be protected against backflow without the necessity to rely on mechanical backflow protection devices.

Please note: if high risk contaminants are likely to be present in a plumbing system, because these represent a greater risk to health, in addition to any point of use protection the water undertaker can also require the installation of zone or wholesite backflow protection.


Regulators Specification: Non-mechanical backflow protection 

Type

Description

Suitability by fluid category 

Back pressure 

Back siphonage 

AA

Air gap with unrestricted discharge above spillover level

5

5

AB

Air gap with weir overflow

5

5

AC

Air gap with vented submerged inlet

3

3

AD

Air gap with injector 

5

5

AF

Air gap with circular overflow

4

4

AG

Air gap with minimum size circular overflow determined by measure or vacuum test

3

3

AUK1

Air gap with interposed cistern 

3

5

AUK2

Air gaps for taps and combination fittings (tap gaps) discharging over domestic sanitary appliances, such as a washbasin, bidet, bath or shower tray shall not be less than the following: 

Size of tap or combination fitting

.

Not exceeding G ½

Exceeding G½ but not exceeding G ¾

Exceeding G ¾

 

Vertical distance bottom of tap outlet above spillover level of recieving appliance

20 mm

25 mm

70 mm

 

X

3

AUK3

Air gaps for taps or combination fittings (tap gaps) discharging over any higher risk domestic sanitary appliances where a fluid category 4 or 5 is present, such as:

  1. any domestic or non-domestic sink or other appliance; or

  1. any appliances in premises where a higher level of protection is required, such as some appliances in hospitals or other health care premises

Shall be not less than 20 mm or twice the diameter of the inlet pipe to the fitting, whichever is the greater

X

5

DC 

Pipe interrupter with permanent atmospheric vent

X

5

Notes:

  1. X Indicates that the backflow prevention arrangement or device is not applicable or not acceptable for protection against backpressure for any fluid category within water installations in the UK.

  2. Arrangements incorporating Type DC devices shall have no control valves on the outlet of the device; they shall be fitted not less than 300 mm (150 mm in Scotland) above the spillover level of a WC pan, or 150 mm above the sparge pipe outlet of a urinal, and discharge vertically downwards 

  3. Overflows and warning pipes shall discharge through, or terminate with, an air gap, the dimension of which should satisfy a Type AA air gap.


Regulators Specification: Mechanical backflow protection 

Type

Description

Suitability by fluid category 

Back pressure 

Back siphonage 

BA

Verifiable backflow preventer with reduced pressure zone

4

4

CA

Non-verifiable disconnector with difference between pressure zones not greater than 10%

3

3

DA

Anti-vacuum valve (or vacuum breaker)

X

3

DB

Pipe interrupter with atmospheric vent and moving element

X

4

DUK1

Anti-vacuum valve combined with a single check valve

2

3

EA

Verifiable single check valve

2

2

EB

Non-verifiable single check valve

2

2

EC

Verifiable double check valve

3

3

ED

Non-verifiable double check valve

3

3

HA 

Hose union backflow preventer. Only permitted for use on existing hose union taps in house installations

2

3

HC

Divertor with automatic return (normally integral with some domestic appliance applications).

X

3

HUK1

Hose union tap which incorporates a double check valve. Only permitted for replacement of existing hose union taps in house installations

3

3

LA

Pressurised air inlet valve

X

2

LB

Pressurised air inlet valve combined with a check valve downstream

2

3

Notes:

  1. X Indicates that the backflow prevention arrangement or device is not applicable or not acceptable for protection against backpressure for any fluid category within water installations in the UK.

  2. Arrangements incorporating a Type DB device shall have no control valves on the outlet of the device. The device shall be fitted not less than 300mm above the spillover level of an appliance and discharge vertically downwards

  3. Types DA and DUK1 shall have no control valves on the outlet of the device and be fitted on a 300 mm minimum Type A upstand.

  4. Relief outlet ports from Types BA and CA backflow prevention devices shall terminate with an air gap, the dimension of which should satisfy a Type AA air gap.

 


Related FAQs

Type AA air gaps

Type AB air gaps

Type AC air gaps

Type AD air gap

Type AF air gaps

Type AG air gaps

Type AUK 1 air gaps

Type AUK2 tap gaps

Type AUK3 tap gaps




Back to all Topics


We use cookies to give you the best possible experience with Water Regs UK. Some are essential to provide website functions and ensure the website is secure. We also use cookies to help us understand how people use the site and to make improvements. Click "Accept All" to enable recommended settings or click "Manage cookies" to adjust your settings. For more details, see our Cookie Policy.